    Default Dirty big variac

    Does anyone have any knowledge of variacs?

    I was wondering if they are stable enough to use to drive my 24VAC lighting.

    I can get a big sucker 240v input(which we have here in New Zealand) and 0-270v output. 1.6KVA

    Could I use this set o 24v as a transformer?

    Apart from the big inrush current when you turn it on are there any other downsides to them?
    <a href="#" onclick="return(showhide(this));">Click here to show display details ...</a>
    <script language="javascript">function showhide(anc){ //
    // traverse forward from anchor to find hidable div:
    for(; ; ){ if(!anc.nextSibling) break; if(anc.nextSibling.nodeName == "DIV") break; anc = anc.nextSibling; }//
    var Y='block', N='none', det=anc.nextSibling; //
    //fall-back plan: use named div:
    if (!det) det=document.getElementById('details'); //
    //toggle visibility:
    det.style.display=(det.style.display!=N)?N:Y; //
    //prevent page refresh:
    return false;}</script><div id="details" style="display:none;">([IMG]https://2881648860440898350-a-1802744773732722657-s-sites.googlegroups.com/site/yatesfamilywebsite/vixensig192.gif?attachauth=ANoY7coHQlbVcJaFiMU4V7JrNBSM4FlneuPA5QnAmzyRC4M6ONTcEqu6GozeGHGOYkETW-mC5xdVPkBgjF99m4buHTlVn65IovMV_jE7YPpEpFmLr3xqJQCk6YFtxsPDmgPt3c9aoNUGPhIM7nutdxnyIpDK3fpqOH1IX3C-vZs8TYojcIGUdxQmuYNKMOCq5yMthsEMP0IBQRifQxDUJ8aNyh_5ypEzlw%3D%3D&attredirects=0[/IMG]
    3 x Grinch with DMX dimming converter and TigerDC48, LEDTRIKS in progress)</div>
    Now a supporting member. I decided it was time to give something back to the forum that has helped me so much.


    Then the Grinch thought of something he hadn't before. What if Christmas, he thought, doesn't come from a store. What if Christmas, perhaps, means a little bit more.

  2. #2
    Join Date
    Oct 2007
    Location
    Bundanoon NSW Australia
    Posts
    226
    Post Thanks / Like

    Default Re: Dirty big variac

    Two major drawbacks.

    As the variac is not isolated the lights will be at mains potential and need to be treated accordingly.

    Variacs do not like to be run at very low percentage settings. You will not be able to get 1.6kVA of load at 24V out of it. (At full load, 1600VA / 240V = 6.6A drawn by the variac). As the variac is just a single winding you basically can only get about the same current out as you put in. i.e. 24V x 6.6A = 160VA. And not the 66A you think you should. The variac will try to supply this load but will only end up letting the magic smoke out.

    Prof.

  3. #3
    Join Date
    Jan 2009
    Location
    New Zealand
    Posts
    414
    Post Thanks / Like

    Default Re: Dirty big variac

    Thanks Prof

    I knew there had to be a good reason they weren't being used.

    Many thanks for the reply
    Steve
    <a href="#" onclick="return(showhide(this));">Click here to show display details ...</a>
    <script language="javascript">function showhide(anc){ //
    // traverse forward from anchor to find hidable div:
    for(; ; ){ if(!anc.nextSibling) break; if(anc.nextSibling.nodeName == "DIV") break; anc = anc.nextSibling; }//
    var Y='block', N='none', det=anc.nextSibling; //
    //fall-back plan: use named div:
    if (!det) det=document.getElementById('details'); //
    //toggle visibility:
    det.style.display=(det.style.display!=N)?N:Y; //
    //prevent page refresh:
    return false;}</script><div id="details" style="display:none;">([IMG]https://2881648860440898350-a-1802744773732722657-s-sites.googlegroups.com/site/yatesfamilywebsite/vixensig192.gif?attachauth=ANoY7coHQlbVcJaFiMU4V7JrNBSM4FlneuPA5QnAmzyRC4M6ONTcEqu6GozeGHGOYkETW-mC5xdVPkBgjF99m4buHTlVn65IovMV_jE7YPpEpFmLr3xqJQCk6YFtxsPDmgPt3c9aoNUGPhIM7nutdxnyIpDK3fpqOH1IX3C-vZs8TYojcIGUdxQmuYNKMOCq5yMthsEMP0IBQRifQxDUJ8aNyh_5ypEzlw%3D%3D&attredirects=0[/IMG]
    3 x Grinch with DMX dimming converter and TigerDC48, LEDTRIKS in progress)</div>
    Now a supporting member. I decided it was time to give something back to the forum that has helped me so much.


    Then the Grinch thought of something he hadn't before. What if Christmas, he thought, doesn't come from a store. What if Christmas, perhaps, means a little bit more.

  4. #4
    Join Date
    Nov 2007
    Location
    Newcastle, Australia
    Posts
    420
    Post Thanks / Like

    Default Re: Dirty big variac

    I have 2 big variacs that I used last year without a problem. 240v input - 0v to 270v output. I had one set to 24v and one set to 36v. Ran approx 10,000 lights from each one. Worked great.
    TC. I could be anything, if I had the talent. :mrgreen:

  5. #5
    Join Date
    Nov 2007
    Location
    Middle Earth
    Posts
    2,260
    Post Thanks / Like

    Default Re: Dirty big variac

    Quote Originally Posted by piesrule58 View Post
    I have 2 big variacs that I used last year without a problem. 240v input - 0v to 270v output. I had one set to 24v and one set to 36v. Ran approx 10,000 lights from each one. Worked great.
    Sure it works, but you need to treat the lights as if they are at mains potential, because between the lights and Earth ( ie you ) they are at mains potential!
    [B][FONT=Arial]stell[COLOR="#FF0000"]a[/COLOR][COLOR="#008000"]s[/COLOR][COLOR="#0000CD"]c[/COLOR]apes[/FONT][/B] - LED lighting solutions for the Prosumer, Commercial and Entertainment Industries.
    Doing pixels first since 2009 with [URL="http://www.youtube.com/watch?v=GAt6A98lXQw"]just another megatree.[/URL]
    Follow us on Facebook at [url]www.facebook.com/stellascapes[/url]
    web: [url]www.stellascapes.com[/url]

  6. #6
    Join Date
    Nov 2007
    Location
    Newcastle, Australia
    Posts
    420
    Post Thanks / Like

    Default Re: Dirty big variac

    Quote Originally Posted by mrpackethead View Post
    Sure it works, but you need to treat the lights as if they are at mains potential, because between the lights and Earth ( ie you ) they are at mains potential!
    Sorry, I am not an electrician and I do not understand what you mean by mains potential.
    BTW, my son is an electrician. He got the variacs for me and set them up. So I assume that they are safe to use.
    TC. I could be anything, if I had the talent. :mrgreen:

  7. #7
    Join Date
    Nov 2007
    Location
    Middle Earth
    Posts
    2,260
    Post Thanks / Like

    Default Re: Dirty big variac

    Quote Originally Posted by piesrule58 View Post
    Sorry, I am not an electrician and I do not understand what you mean by mains potential.
    BTW, my son is an electrician. He got the variacs for me and set them up. So I assume that they are safe to use.
    THe voltage across teh load ( the lamps ) may be 24V, but the voltage between phase and earth could be at 240V ( mains potential ).. So if you were to come into contact with one of the wires, you may be in for a shocking suprize!

    A variac only has one winding, with multiple taps. Your electrican son should know better than to do this. Are you sure you've got a variac?
    [B][FONT=Arial]stell[COLOR="#FF0000"]a[/COLOR][COLOR="#008000"]s[/COLOR][COLOR="#0000CD"]c[/COLOR]apes[/FONT][/B] - LED lighting solutions for the Prosumer, Commercial and Entertainment Industries.
    Doing pixels first since 2009 with [URL="http://www.youtube.com/watch?v=GAt6A98lXQw"]just another megatree.[/URL]
    Follow us on Facebook at [url]www.facebook.com/stellascapes[/url]
    web: [url]www.stellascapes.com[/url]

  8. #8
    Join Date
    Feb 2008
    Location
    Moultrie, Georgia
    Posts
    390
    Post Thanks / Like

    Default Re: Dirty big variac

    Wouldn't an isolated variac eliminate this problem? I used one for years when I was an electronics repair tech. I think they changed the name now to variable transformer but years ago the were called isolated variacs.

  9. #9
    Join Date
    May 2007
    Location
    Apple Valley, MN
    Posts
    3,536
    Post Thanks / Like

    Default Re: Dirty big variac

    VARIAC is a trade name. It originally stood for ‘Vary AC’. ‘Variable Transformer’ is just another name for the same thing.

    There are isolated VARIAC’s but they’re not very common. You could use a 1:1 isolation transformer on the input or output but they’re just as expensive as the VARIAC.

    It is possible to use two transformers back to back, i.e. tie the secondaries together and use the primaries as input and output. The higher the secondary voltage, the higher the current will be for a given size. This will at least provide isolation.

    Personally when I use a VARIAC while testing, I just know not to be touching anything that I wouldn’t if it was plugged in directly.
    A mediocre person tells. A good person explains. A superior person demonstrates. A great person inspires others to see for themselves.

    Click here to show/hide my display details ...
    Click here to show/hide DIYC Links ...

  10. #10
    Join Date
    Nov 2007
    Location
    Middle Earth
    Posts
    2,260
    Post Thanks / Like

    Default Re: Dirty big variac

    Quote Originally Posted by ErnieHorning View Post
    VARIAC is a trade name. It originally stood for ‘Vary AC’. ‘Variable Transformer’ is just another name for the same thing.
    Check out "autotransformer" at wikipedia for a good explaination.
    [B][FONT=Arial]stell[COLOR="#FF0000"]a[/COLOR][COLOR="#008000"]s[/COLOR][COLOR="#0000CD"]c[/COLOR]apes[/FONT][/B] - LED lighting solutions for the Prosumer, Commercial and Entertainment Industries.
    Doing pixels first since 2009 with [URL="http://www.youtube.com/watch?v=GAt6A98lXQw"]just another megatree.[/URL]
    Follow us on Facebook at [url]www.facebook.com/stellascapes[/url]
    web: [url]www.stellascapes.com[/url]