| (24 intermediate revisions by 3 users not shown) | |||
| Line 6: | Line 6: | ||
:The following procedures require the individual to be familiar with the operation of a digital multimeter (or voltmeter/ohmmeter if you prefer).  If you currently do not know how to measure resistance or how to measure voltage, please take some time now an learn these basic skills before attempting these procedures.  This [http://www.  | :The following procedures require the individual to be familiar with the operation of a digital multimeter (or voltmeter/ohmmeter if you prefer).  If you currently do not know how to measure resistance or how to measure voltage, please take some time now an learn these basic skills before attempting these procedures.  This [http://www.ladyada.net/learn/multimeter/ website] provides some basic information on using multi-meters.  They have different types and model and even have a few videos!  | ||
| Line 12: | Line 12: | ||
! <center>'''Multimeter Usage Tip'''</center>  | ! <center>'''Multimeter Usage Tip'''</center>  | ||
| All DC voltages in this document are referenced to GND.  So for all measurements, the multimeter negative (-) lead, usually black, needs to be connected to a GND point on the PCB.  The best location would be the GND Test Point TP1 located near RJ45 Jack   | | All DC voltages in this document are referenced to GND.  So for all measurements, the multimeter negative (-) lead, usually black, needs to be connected to a GND point on the PCB.  The best location would be the [[media:Renard 64XC TP1.jpg |GND Test Point TP1]] located near RJ45 Jack J21.  The positive lead (+), usually red, gets connected to the location called out in the procedure.  | ||
| Line 34: | Line 34: | ||
==='''Most Common Problems'''===  | ==='''Most Common Problems'''===  | ||
:These are the most common problems encountered by individuals who have built Renard   | :These are the most common problems encountered by individuals who have built Renard boards since their debut to the DIYC community:  | ||
| Line 47: | Line 47: | ||
::*'''Incorrect Vixen Settings'''.  It cannot be emphasized enough, the Renard boards will not work correctly if Vixen is not setup correctly.  Verify that you have the Vixen plug-in settings correct as compared to the [[Renard_64XC#Computer Setup | Renard 64XC Controller wiki]].  The settings in Vixen   | ::*'''Incorrect Vixen Settings'''.  It cannot be emphasized enough, the Renard boards will not work correctly if Vixen is not setup correctly.  Verify that you have the Vixen plug-in settings correct as compared to the [[Renard_64XC#Computer Setup | Renard 64XC Controller wiki]].  The settings in Vixen must match the setting used in the Renard Firmware burned onto the PICs.  | ||
=='''Troubleshooting  the Renard 64XC Controller'''==  | =='''Troubleshooting  the Renard 64XC Controller'''==  | ||
| Line 241: | Line 241: | ||
[[Image: Transfomer.png|600px|center]]  | [[Image: Transfomer.png|600px|center]]  | ||
<li>Connect one SSR each to J12 and J8 with a known [[Media:CAT5_Cable_Testing.png |good CAT5 cable]].  Now, the link is a diagram of how to check for continuity in a cable.  Here is how to use a [http://www.ladyada.net/learn/multimeter/continuity.html multimeter] to do just that.  | |||
<li>Turn ON the AC Power to the Renard Board  | <li>Turn ON the AC Power to the Renard Board  | ||
| Line 254: | Line 256: | ||
:*If it did, go to step XXXXXX.....(???)  | :*If it did, go to step XXXXXX.....(???)  | ||
<li>Measure DC voltage at U1.  This is the lead closest to   | <li>Measure DC voltage at U1.  This is the lead closest to [[Media:Renard 64XC 5VDC Testpoint.jpg | U4.]]  | ||
:Voltage should be +5 VDC +/- 0.05  | :Voltage should be +5 VDC +/- 0.05  | ||
:*If incorrect, go to step 13(??)    | :*If incorrect, go to step 13(??)    | ||
| Line 261: | Line 263: | ||
:*If it did, go to step 21(??)  | :*If it did, go to step 21(??)  | ||
<li>Measure DC voltage on   | <li>Measure DC voltage on [[media:Renard 64XC R19 Measurements.jpg | output side of R19]].  This is the end closest to  the Power LED.     | ||
:*If voltage is approx. 2.0-3.0 VDC, replace the LED and retest  | :*If voltage is approx. 2.0-3.0 VDC, replace the LED and retest  | ||
:*If voltage is approx. 5.0 VDC, then either the LED is installed backwards or it is bad  | :*If voltage is approx. 5.0 VDC, then either the LED is installed backwards or it is bad  | ||
<li>Measure DC voltage on   | <li>Measure DC voltage on [[media:Renard 64XC R19 Measurements.jpg  | input side of R19]].  This is the end furtherest away from the Power LED.     | ||
:Voltage should be approx. 5.0 VDC.  | :Voltage should be approx. 5.0 VDC.  | ||
:*If correct, then double check the value of R19 and/or replace R19.  | :*If correct, then double check the value of R19 and/or replace R19.  | ||
:*If this is incorrect, restart the troubleshooting process.  | :*If this is incorrect, restart the troubleshooting process.  | ||
<li>Measure DC voltage at   | <li>Measure DC voltage at the [[media:Renard 64XC D1-D2 Measurement.jpg | cathodes of D1 & D2]].     | ||
:Voltage should be above +6 VDC but less than +12 VDC.  | :Voltage should be above +6 VDC but less than +12 VDC.  | ||
:*If correct, voltage regulator U1 is probably bad or installed backwards.    | :*If correct, voltage regulator U1 is probably bad or installed backwards.    | ||
<li>Measure AC voltage   | <li>Measure AC voltage [[media:Renard 64XC R1-R2 Measurement.jpg | between R1 and R2]].  | ||
:Voltage should be above 6 VAC    | :Voltage should be above 6 VAC    | ||
:*If correct, one or more diodes D1 thru D4 could be bad or incorrectly installed (backwards).  | :*If correct, one or more diodes D1 thru D4 could be bad or incorrectly installed (backwards).  | ||
<li>Measure AC voltage between   | <li>Measure AC voltage between the power terminals [[media:Renard 64XC Power Terminals Measurement.jpg | Tab1 & Tab2]].  | ||
:Voltage should be between 6.3VAC and 7.4VAC.    | :Voltage should be between 6.3VAC and 7.4VAC.    | ||
:*If incorrect, transformer is probably bad or wired incorrectly.  | :*If incorrect, transformer is probably bad or wired incorrectly.  | ||
| Line 438: | Line 440: | ||
==='''Verifying Diagnostic LEDs'''===    | ==='''Verifying Diagnostic LEDs'''===    | ||
A reminder that the diagnostic LEDs referred to here are the CHANNEL LEDs associated with Channels 1-8.  The Renard 64XC does not need special LEDs as they should already be installed.  | |||
<ol>  | <ol>  | ||
<li>Turn OFF AC power    | <li>Turn OFF AC power    | ||
<li>Remove PIC chip   | <li>Remove PIC chip U10   | ||
<li>Turn ON AC power    | <li>Turn ON AC power    | ||
<li>Power LED should be lit and the DC voltage at the [[media:Wiki - TSG Renard SS24 Meas01.gif |+5 Test Point]] should be 5.0 (+/- .5) VDC.    | <li>Power LED should be lit and the DC voltage at the <!--[[media:Wiki - TSG Renard SS24 Meas01.gif |+5 Test Point]]--> should be 5.0 (+/- .5) VDC.    | ||
:*If incorrect , then go to [[  | :*If incorrect , then go to [[Troubleshooting_Guide_Renard_64XC#Troubleshooting_Power_Problems | Troubleshooting Power Problems]]  | ||
<li>Momentarily connect a jumper (small piece of wire) between   | <li>Momentarily connect a jumper (small piece of wire) between U10 [[media: Wiki - IC socket 13-14.jpg | IC socket pin 13 and pin 14]]    | ||
:*HB LED should light  | :*HB LED should light  | ||
<li>Momentarily connect a jumper between   | <li>Momentarily connect a jumper between U10 [[media: Wiki - IC socket 10-14.jpg | IC socket pin 10 and pin 14]]  | ||
:*ZC LED should light  | :*ZC LED should light  | ||
<li>Momentarily connect a jumper between   | <li>Momentarily connect a jumper between U10 [[media: Wiki - IC socket 9-14.jpg | IC socket pin 9 and pin 14]]  | ||
:*SD LED should light  | :*SD LED should light  | ||
<li>Momentarily connect a jumper between   | <li>Momentarily connect a jumper between U10 [[media: Wiki - IC socket 8-14.jpg | IC socket pin 8 and pin 14]]    | ||
:*FE LED should light  | :*FE LED should light  | ||
<li>Momentarily connect a jumper between   | <li>Momentarily connect a jumper between U10 [[media: Wiki - IC socket 7-14.jpg | IC socket pin 7 and pin 14]]    | ||
:*OE LED should light  | :*OE LED should light  | ||
| Line 469: | Line 472: | ||
<li>If all of the LEDs in steps 6 thru 10 did not light:  | <li>If all of the LEDs in steps 6 thru 10 did not light:  | ||
:a.  Check for 5.0 VDC at [[media:Wiki - TSG Renard SS U6 5VDC Check (top).jpg | U6 IC socket pin 1]]  | :a.  Check for 5.0 VDC at [[media:Wiki - TSG Renard SS U6 5VDC Check (top).jpg | U6 IC socket pin 1]]  | ||
::*If incorrect, check the solder pads and/or go back to [[  | ::*If incorrect, check the solder pads and/or go back to [[Troubleshooting_Guide_Renard_64XC#Troubleshooting_Power_Problems | Troubleshooting Power Problems]]  | ||
:b  | :b.  Check for 5.0 VDC at [[media:Wiki - TSG Renard SS JP3 Check.jpg | left side of JP3]]  | ||
::*If incorrect, check the solder pads    | ::*If incorrect, check the solder pads    | ||
:  | :c.  Install shunt on JP3  | ||
:  | :d.  Check for 5.0 VDC at [[media:Wiki - TSG Renard SS JP3 Check (OUT).jpg | right side of JP3]] (on underside of board).  | ||
::*If incorrect, replace the shunt (jumper)    | ::*If incorrect, replace the shunt (jumper)    | ||
:  | :e.  Check for approx. 5.0 VDC on the [[media:Wiki - TSG Renard SS RN1 Check.jpg | pins (on underside of board) of resistor network RN1]].  | ||
::*If correct, then probably all the LEDs are installed backwards  | ::*If correct, then probably all the LEDs are installed backwards  | ||
::*If incorrect, replace RN1  | ::*If incorrect, replace RN1  | ||
<li>If any (but not all) of the LEDs in steps 6 thru 10 did not light, measure the DC voltage at the appropriate location on the IC socket for   | <li>If any (but not all) of the LEDs in steps 6 thru 10 did not light, measure the DC voltage at the appropriate location on the IC socket for U10.  The voltage measured at each location should be approximately 3.0-3.5 VDC.  | ||
| Line 486: | Line 488: | ||
{| border="1" cellpadding="5" style="text-align: center; margin: 1em auto 1em auto"     | {| border="1" cellpadding="5" style="text-align: center; margin: 1em auto 1em auto"     | ||
!width="150"|    | !width="150"| Diagnostic LED  | ||
!width="250"|    | !width="250"|  Measure DC voltage at  | ||
|HB ||  | |HB ||U10 [[media:Wiki - 14 Pin IC Socket 13.jpg | IC socket pin 13]]  | ||
|ZC ||  | |ZC ||U10 [[media:Wiki - 14 Pin IC Socket 10.jpg | IC socket pin 10]]  | ||
|SD ||  | |SD ||U10 [[media:Wiki - 14 Pin IC Socket 9.jpg | IC socket pin 9]]    | ||
|FE ||  | |FE ||U10 [[media:Wiki - 14 Pin IC Socket 8.jpg | IC socket pin 8]]  | ||
|OE ||  | |OE ||U10 [[media:Wiki - 14 Pin IC Socket 7.jpg | IC socket pin 7]]  | ||
<br>  | <br>  | ||
| Line 513: | Line 513: | ||
=='''Troubleshooting SSR Circuitry Problems'''==    | =='''Troubleshooting SSR Circuitry Problems'''==    | ||
If the troubleshooting process points here, then you need to be looking at whatever external SSRs that are connected to the Renard 64XC.  Basically, the functionality of the controller has been verified and the problem most likely is in the external connections or components.  | |||
The Troubleshooting Guide for the SSRez can be found [[SSRez#Troubleshooting | here.]]  | |||
==='''Symptom(s): '''===  | ==='''Symptom(s): '''===  | ||
:*Channel remains on constantly  | :*Channel remains on constantly  | ||
| Line 519: | Line 524: | ||
==='''Possible Problem(s): '''===    | ==='''Possible Problem(s): '''===    | ||
:*Bad   | :*Bad TRIAC  | ||
:*  | :*TRIAC in Backwards  | ||
:*Bad   | :*Bad Opto/MOC  | ||
:*Opto/MOC in Backwards  | :*Opto/MOC in Backwards  | ||
:*Bad/missed Solder Joints  | :*Bad/missed Solder Joints  | ||
| Line 850: | Line 855: | ||
[[Category:Renard 64XC]]  | |||
[[Category:  | [[Category:DIYC Index]]  | ||
Latest revision as of 04:22, 29 January 2011
- The following procedures require the individual to be familiar with the operation of a digital multimeter (or voltmeter/ohmmeter if you prefer). If you currently do not know how to measure resistance or how to measure voltage, please take some time now an learn these basic skills before attempting these procedures. This website provides some basic information on using multi-meters. They have different types and model and even have a few videos!
| All DC voltages in this document are referenced to GND. So for all measurements, the multimeter negative (-) lead, usually black, needs to be connected to a GND point on the PCB. The best location would be the GND Test Point TP1 located near RJ45 Jack J21. The positive lead (+), usually red, gets connected to the location called out in the procedure. |
Basic Troubleshooting Info
Verify Setup
- These are the most common problems encountered by individuals who have built Renard boards since their debut to the DIYC community:
- Incorrect Vixen Settings. It cannot be emphasized enough, the Renard boards will not work correctly if Vixen is not setup correctly. Verify that you have the Vixen plug-in settings correct as compared to the Renard 64XC Controller wiki. The settings in Vixen must match the setting used in the Renard Firmware burned onto the PICs.
Troubleshooting Flow
Troubleshooting Steps
 - Turn ON AC power
 - PWR LED should be lit
 - Run a Vixen sequence
- If they do, go to step 15
 - Turn OFF AC power
 - Swap PIC chips U10 and U9
 - Turn ON AC power
 - Turn OFF AC power
 - Swap PIC chips U10 and U8
 - Turn ON AC power
 - Turn OFF AC power
 - Swap PIC chips U10 and U7
 - Turn ON AC power
 - Turn OFF AC power
 - Swap PIC chips U10 and U14
 - Turn ON AC power
 - Turn OFF AC power
 - Swap PIC chips U10 and U13
 - Turn ON AC power
 - Turn OFF AC power
 - Swap PIC chips U10 and U12
 - Turn ON AC power
 - Turn OFF AC power
 - Swap PIC chips U10 and U11
 - Turn ON AC power
Symptom(s):
- PWR LED not lit
 - IC Chips hot to the touch
- No Input Voltage Present
 - Transformer Bad
 - Voltage Regulator Bad
 - Diode Polarity Wrong
 - Capacitor Polarity Wrong
 - LED installed backwards
 - Disconnect all cables.
 - In normal use, the Renard 64XC does not require a fuse.  However, since this section is about "problems", it is prudent to have one installed.  The best way to do this is with an in-line fuse holder on the incoming power.  Mouser PN#576-150274 (holder) and PN#576-0235.300MXP (fuse) are perfect for this. The fuse used in a 300mA fuse and is rated much smaller than the power requirements of the Renard 64XC during normal use.  However, using a smaller fuse here is for safety during initial power testing. If there are any problems with bridged solder pads or a bad transformer during first power application, a small fuse will blow before any permanent damage to the SSR PCB can occur.
 - Connect one SSR each to J12 and J8 with a known good CAT5 cable. Now, the link is a diagram of how to check for continuity in a cable. Here is how to use a multimeter to do just that.
 - Did the SSR fuse blow?
 - Did the in-line fuse blow?
- If it did, go to step XXXXXX.....(???)
 - Measure DC voltage at U1.  This is the lead closest to  U4.
 - Did the PWR LED light Up?
 - Measure DC voltage on  output side of R19.  This is the end closest to  the Power LED.
 - If voltage is approx. 5.0 VDC, then either the LED is installed backwards or it is bad
 - Measure DC voltage on  input side of R19.  This is the end furtherest away from the Power LED.
- If correct, then double check the value of R19 and/or replace R19.
 - Measure DC voltage at the  cathodes of D1 & D2.
 - Measure AC voltage between the power terminals  Tab1 & Tab2.
- Voltage should be between 6.3VAC and 7.4VAC.
- If incorrect, transformer is probably bad or wired incorrectly.
 - Measure AC voltage between  the inline filter closest to the transformer and Tab1.
- If correct, the in-line fuse is probably bad.
 - Turn OFF SSR AC power
 - Remove F1 from the SSR
 - Turn ON SSR AC power
 - Recheck SSR AC voltage between and any N terminal.
- Bad/shorted triac
- Carefully inspect the SSR board for any possible problems with the solder connections. Fix any possible problems and then restart the troubleshooting process.
 - After other attempts to fix the problem have failed, the last resort would be to remove each triac from the SSR til good power was seen with F1 installed.
 - Turn OFF AC power
 - Turn ON AC power
 - Did the PWR LED light?
Symptom(s):
 - HB and ZC LED do not flash
 - FE and/or OE LEDs light
- Oscillator bad
 - Zero Cross signal bad
 - R1/R2 are the Wrong Value
 - Vixen settings incorrect
 - PIC bad
- Turn OFF AC power
 - Remove PIC chip U6
 - Turn ON AC power
 - The  Beta Renard Diagnostic Firmware should perform the following channel test:
- Replace U2
 - Check the values of R1 & R2
REMINDER:
NOTE:
 - SD LED will be ON whenever Vixen sends data to the Renard SS24.  The FE and OE LEDs should remain OFF.
 - Replace U5
- Turn OFF AC power
 - Remove PIC chip U10
 - Turn ON AC power
 - Power LED should be lit and the DC voltage at the  should be 5.0 (+/- .5) VDC.
 - Momentarily connect a jumper (small piece of wire) between U10  IC socket pin 13 and pin 14
- HB LED should light
 - Momentarily connect a jumper between U10  IC socket pin 10 and pin 14
- ZC LED should light
 - Momentarily connect a jumper between U10  IC socket pin 9 and pin 14
- SD LED should light
 - Momentarily connect a jumper between U10  IC socket pin 8 and pin 14
- FE LED should light
 - Momentarily connect a jumper between U10  IC socket pin 7 and pin 14
- OE LED should light
 - b.  Check for 5.0 VDC at  left side of JP3
 - c. Install shunt on JP3
 - d.  Check for 5.0 VDC at  right side of JP3 (on underside of board).
 - e.  Check for approx. 5.0 VDC on the  pins (on underside of board) of resistor network RN1.
 - If incorrect, replace RN1
 - If any (but not all) of the LEDs in steps 6 thru 10 did not light, measure the DC voltage at the appropriate location on the IC socket for U10.  The voltage measured at each location should be approximately 3.0-3.5 VDC.
Diagnostic LED Measure DC voltage at HB U10 IC socket pin 13 ZC U10 IC socket pin 10 SD U10 IC socket pin 9 FE U10 IC socket pin 8 OE U10 IC socket pin 7
The Troubleshooting Guide for the SSRez can be found here.
Symptom(s):
- Bad TRIAC
 - TRIAC in Backwards
 - Bad Opto/MOC
 - Opto/MOC in Backwards
 - Bad/missed Solder Joints
- Turn OFF AC power
 - Are channels 13 thru 24 bad?  If they are,
- Check the right side fuse
- If not, go to step 21
 - Turn ON AC power
 - Test lights should be OFF
- Turn OFF AC power
 - Install PIC chip U6
 - Turn OFF AC power
 - Turn OFF AC power
 - Turn ON AC power
SAFETY NOTICE:
- Bad triac
- It should be 5 VDC
- If not, go to step 37
 - Remove PIC chip U7
 - Turn ON AC power
- Turn OFF AC power
 - Install PIC chip U7
 - Turn OFF AC power
 - Turn OFF AC power
 - Turn ON AC power
SAFETY NOTICE:
- Bad triac
 - Remove PIC chip U8
 - Turn ON AC power
- Turn OFF AC power
 - Install PIC chip U8
 - Turn OFF AC power
 - Turn OFF AC power
 - Turn ON AC power
SAFETY NOTICE:
- Bad triac
 - Turn OFF AC power
 - Turn ON AC power
 - Is the test light still ON?