Line 292: | Line 292: | ||
==Firmware Version 3.x Configuration== | ==Firmware Version 3.x+ Configuration== | ||
[[File:BridgeConfigPage.png]] | |||
===System Settings=== | |||
[[File:SystemSettings.png]] | |||
IP Mode: Sets Static or DHCP IP address Mode<br/> | |||
IP Address: The IP Address of the Bridge<br/> | |||
Subnet Mask: The Subnet Mask of the Bridge<br/> | |||
Gateway: The Gateway Address<br/> | |||
MAC Address: The MAC Address of the MAC IC or Auto generated MAC Address<br/> | |||
Mode: Sets the Bridge in Multicast or Unicast Mode<br/> | |||
After making changes to any of the settings above click "Update System Settings" to save these setting. | |||
===Universe Settings=== | |||
[[File:UniverseNumbers.png]] | |||
Universe Number: Defines the Universe numbers the Bridge will use, 6 are available in Multicast Mode (Unusable ones are grayed out) and 12 are available in Unicast Mode. All numbers should be unique.<br/> | |||
Packets Received: The number of packages received on this universe.<br/> | |||
DMX Channel Count: The number of channels sent in the E1.31 Universe packet.<br/> | |||
Sequence Errors: The number of out of order packets received. NOTE: There is a bug in some of the transmitting E1.31 plugins where sequence numbers are not sequential per Universe. <br/> | |||
After making changes to the Universe numbers above click "Update Universe Numbers" to save these setting. | |||
===Output Configuration=== | |||
[[File:OutputConfiguration.png]] | |||
Output Number: The output jack number.<br/> | |||
Protocol: The Protocol used for the output.<br/> | |||
Baud (Renard Only): Sets the Renard Output Serial Baud Rate.<br/> | |||
Options (Renard Only): Defines the output formate, Normally use 8N1, 8M2 is for solving issues with higher channel counts for RenW setups.<br/> | |||
Channels: The number of channels on this output. (Note DMX has a max of 512 Channels)<br/> | |||
Start Universe: Define the universe number of the starting channel.<br/> | |||
Start Channel: The starting channel for this output.<br/> | |||
End Universe: Auto calculated ending Universe Number.<br/> | |||
End Channel: Auto calculated ending Channel Number.<br/> | |||
After making changes to each output number click "Update" to save the changes for that output. | |||
==Firmware Version 2.x Configuration Commands== | ==Firmware Version 2.x Configuration Commands== |
Revision as of 01:22, 21 January 2014
The 6-port E1.31 bridge is a device that allows your PC to communicate with a large number of Renard or DMX controllers using regular Ethernet network connections. It replaces multiple DMX or RS485 dongles with one configurable device that can be mounted in an enclosure in the yard and only requires one Ethernet Cat5 cable (or WIFI) back to your pc or home network. It allows up to 6 DMX universes or Renard networks to be easily controlled from your sequencing software with a minimum amount of wire from your show pc to your controllers. The bridge works with all Renard, DMX and LOR (using DMX) controllers.
The 6-port E1.31 bridge is a device that takes in an E1.31 stream from your network and converts (or 'bridges') that to multiple DMX or Renard output streams. E1.31 or sACN (Streaming Architecture for Control Networks) is a method of multiplexing multiple DMX streams over your network using unicast or multicast UDP packets. The 6-port bridge currently only supports multicast streams. This makes it simpler to configure but has drawbacks in very large configurations (10's of streams). E1.31 can support 63,999 DMX streams or 'universes' (64000->65536 are reserved) so it has a virtually unlimited amount of expansion available.
The Parallax Propeller microcontroller determines if the address matches one of the configured ports universe numbers and if it does, reads in the entire DMX stream and sends them out that particular port either as-is or after conversion to Renard protocol. The Propeller chip is quite powerful, it is essentially eight separate microcontrollers in a single package. These internal processors or COGs as they are called can each run completely different (or the same) code. This allows you to partition different functions to different COGs within your code. For more information on the Propeller, visit the Parallax site.
E1.31 Networking Basics and Setup
For more information about how E1.31 works and how you wire up the IP networking side of an E1.31 Network look at E1.31 Protocol
6 Port E1.31 Bridge Parts
To build the E1.31 Bridge, you need 4 things:
- The PCB
- The parts to solder on the board, also known as a BOM (Bill Of Materials).
- A power supply to power the board. The board can use any 5-24VDC power supply.
- An enclosure to mount the finished board in. Commonly used enclosures include the CG-500, CG-1000 or the CG-2000 which are available from several vendors
Mouser BOM | |||
Part ID | Mouser PN | Description | Qty |
R1-R3 | 291-220-RC | Carbon Film Resistors - Through Hole 220ohms 0.05 | 3 |
R4-R9 | 291-120-RC | Carbon Film Resistors - Through Hole 120ohms 0.05 | 6 |
R10-R12 | 291-10K-RC | Carbon Film Resistors - Through Hole 10Kohms 0.05 | 3 |
C1-C3 | 140-REA470M1VBK0611P | Aluminum Electrolytic Capacitors - Leaded 35V 47uF 20% 6.3x11mm | 3 |
C4-C12 | 581-SA105E104MAR | Multilayer Ceramic Capacitors MLCC - Leaded 50volts 0.1uF 20% Z5U | 9 |
IC1 | 619-P8X32A-D40 | 32-bit Microcontrollers - MCU DIP pkg Propeller Chip | 1 |
IC2 | 579-24LC512-I/P | EEPROM 64kx8 - 2.5V | 1 |
IC3-IC8 | 511-ST485BN | Buffers & Line Drivers Hi-Spd Lo Pwr Trans | 6 |
IC9 | 579-24AA025E48-I/SN | EEPROM 2K 256 X 8 1.8V SERIAL EE, IND | 1 |
X1 | 520-HCU500-20X | Crystals 5MHz 20pF | 1 |
Wiznet | 950-WIZ820IO | Ethernet Modules W5200 & MAG JACK ioPLATFORM MODULE | 1 |
LED1 | 604-WP7113GD | 604-WP7113GD | 1 |
LED2-LED3 | 604-WP7113ID | Standard LEDs - Through Hole HI EFF RED DIFFUSED | 2 |
VR1 | 580-OKI78SR5/1.5W36C | DC/DC Converters 7.5W 24Vin 5Vout1 1.5A SIP Non-Iso | 1 |
VR2 | 511-LF33CV | Low Dropout Regulators - LDO 3.3V 0.5A Positive | 1 |
Heatsink | 532-577202B00 | Heat Sinks TO-220 HORIZ/VERT SLIM CHANNEL STYLE | 1 |
S1-S2 | 653-B3F-1000 | Tactile Switches 6X6 Flat 4.3mm Btn Force 100g w/o Grd | 2 |
IC Socket 1 | 575-199640 | IC & Component Sockets 40P TIN PIN TIN CONT | 1 |
IC Socket 2 - IC Socket 8 | 575-1104331610003000 | IC & Component Sockets 8P DIP SOCKET SOCKETS | 7 |
JP1 | 571-826629-3 | Headers & Wire Housings 3P SINGLE ROW | 1 |
H1 | 571-826629-4 | Headers & Wire Housings 4P SINGLE ROW | 1 |
Wiznet 1x6 Header | 517-9601066202AR | Headers & Wire Housings 6P STR SR BDMNT SKT 3.0MM TAIL/7.1MMBODY | 2 |
2x3 Output Selector | 855-M20-9980345 | Headers & Wire Housings 03+03 DIL VERTICAL PIN HEADER GOLD HT | 12 |
TB1 | 571-2828372 | Fixed Terminal Blocks 5.08MM PCB MOUNT 2P | 1 |
J1-J6 | 571-5556416-1 | 571-5556416-1 | 6 |
Output Shunts | 517-9691020000DA | Headers & Wire Housings 2.54MM SHUNT | 25 |
You can buy the parts directly from Mouser: Click here for Mouser Direct Project BOM
or
The BOM is also available at a discount in a kit that includes the PCB from DIYLEDExpress.com
The 6 Port E1.31 Bridge requires a fair bit of soldering so take your time and ensure you install the components in the correct orientation when required. Start by sorting the components by type and values. Look over the PCB before starting noting the location of the various components. Follow the standard procedure of installing the lowest profile parts first and ending up with the tallest. You can click on any photo to see a larger version of the image.
- □ Install the MAC IC, this is the only surface mount IC. It is optional if you are not comfortable with soldering surface mount ICs. The firmware will generate a random MAC ID if the IC is not installed. The IC is polarized and the IC must be installed so that the dot on the package aligns with the dot on the pcb, the lower right side of the pad. For hints on how to solder a SMT device look here.
- □ Install the nine 0.1uF (100nF) capacitors C4-C12. The capacitors are not polarized and can be mounted either way.
- □ Install the three 220 Ohm resistors (red, red, brown, gold) R1-R3. The resistors are not polarized and can be mounted either way.
- □ Install the six 120 Ohm resistors (brown, red, brown, gold) R4-R9. The resistors are not polarized and can be mounted either way.
- □ Install the three 10K Ohm resistors (brown, black, orange, gold) R10-R12 The resistors are not polarized and can be mounted either way.
- □ Install the 5Mhz Crystal X1. The crystal is not polarized and can be mounted either way.
- □ Install the two push button switches S1-S2. The switches are polarized and will only fit on the board one way.
- □ Install the seven 8 pin IC sockets. The sockets are polarized and have a notch on one end. It should be mounted so that the notch is oriented to the left and matching the marking on the pcb.
- □ Install the one 40 pin socket. The sockets are polarized and have a notch on one end. It should be mounted so that the notch is oriented to the right and matching the marking on the pcb.
- □ Install the green ACT LED (LED1). Note that the LED is polarized and the long lead should face towards the top of the board. Note: silkscreen shows "FLAT" side of the LED, this can also be used to check for proper orientation
- □ Install the two red STATUS and POWER LEDs (LED2-LED3). Note that the LED is polarized and the long lead should face towards the top of the board. Note: silkscreen shows "FLAT" side of the LED, this can also be used to check for proper orientation
- □ Install the 3.3V Regulator VR2 with the heat sink. The voltage regulator is polarized and goes only one way. Gently bend the leads of the regulator at the location on the leads where it changes size down at a 90 degree angle towards the flat side of the regulator. Apply thermal grease to the flat heat sink side of the regulator and the heatsink and fasten it to the pcb using a #4 screw and nut.
- □ Install the 3 Pin headers JP1. The short end of the header is soldered to the pcb.
- □ Install the 4 Pin headers H1. The short end of the header is soldered to the pcb.
- □ Install the two WizNet 1x6 pin headers.
- □ Install the twelve 2x3 output selector pin headers. The short end of the headers are soldered to the pcb.
- □ Install the power terminal block TB1. Install so that the wire openings face the edge of the pcb.
- □ Install the three 47uF Capacitors C1-C3. The capacitors are polarized and can only be installed one way. The side of the capacitor will have a stripe on the negative side. The long lead is the positive side, and it goes in the hole marked with a + to the right.
- □ Install the DC-DC Converter VR1. The voltage regulator is polarized and must only be installed one way. The flat side of the voltage regulator must be mounted towards the bottom of the board, aligning with the stripe on the pcb.
- □ Install the six RJ45 jacks J1-J6. The jacks are polarized and they have to be installed with the correct orientation. Gently install all 8 pins into the holes and them firmly press down on the socket to seat the plastic pins in the holes in the PCB.
- □ Install the six RT485BN in IC3-IC8 with the notches facing the left edge with the power terminal block.
- □ Install the EEPROM in IC2 with the notch facing the left edge with the power terminal block.
- □ Install the Propeller in IC1 with the notch facing the WizNet adapter to the right.
- □ Install the WizNet adapter with the RJ45 socket facing the Propeller IC.
Jumpers
Power Jumper - JP1
Output Configuration Jumpers
Each port has a set of four separate jumpers. These jumpers set the wiring configuration on their respective output jacks. If you want a DMX wiring output, you need to put all four jumpers to the "DMX" side. If you want a Renard wiring output, you need to put all four jumpers to the "REN" side. It is important that all four jumpers are in the same position for that port. Note that the protocol for the port is different than the wired output. You must set the DMX or Renard output protocol via the Bridge configuration settings.
Output Jumper Settings | ||
Pin # | RJ45 Connectors | |
REN | DMX | |
1 | SIGNAL GND | RS-485 DATA+ |
2 | SIGNAL GND | RS-485 DATA- |
3 | NC | NC |
4 | RS-485 DATA- | NC |
5 | RS-485 DATA+ | NC |
6 | NC | NC |
7 | NC | SIGNAL GND |
8 | NC | NC |
You can use the bridge to drive LOR controllers capable of supporting DMX as well. The simplest method is to configure the software protocol for DMX and use the REN output jumper settings. You will be required build a jumper cable to swap pins 4 and 5 between the two ends of the jumper because LOR has these signals swapped. You may also want to connect pin 6 from the LOR to pins 1 or 2 if using the REN output.
Powering the E1.31 Bridge
As mentioned above, the bridge can be powered with either a well regulated +5vdc supply or an unregulated/regulated +7-24vdc supply. The power supply should supply at least 350 mA. Configure the power jumper appropriately before applying power.
Initial Testing
Power up LED Activity
On initial power up the green ACT and the red STATUS LEDs flash a sequence of codes to help identify the status and configuration of the bridge. After they go thru their startup flash sequence, the the green ACT LED flashes when ever it sees IP data traffic and the red LED stays lit to signify that the configuration webpage is accessible. The Green ACT LED startup flash pattern are:
Green ACT LED Startup Flash Count | |
# of Flashes | |
IP Status | |
1 | The default bridge IP address mode is DHCP and the bridge acquired an IP address from a DHCP server. |
2 | The default bridge IP address mode is STATIC and the STATIC address programmed into the bridge is being used. |
3 | The default bridge IP address mode has been overridden due to a button press and the bridge has acquired an IP address from a DHCP server. |
4 | The default bridge IP address mode has been overridden due to a button press and the STATIC address programmed into the bridge is being used. |
5 | The default bridge IP address mode is DHCP and has been overridden due to no response from the DHCP server and the IP address of 169.254.74.73 is being used. |
7 | The default bridge IP address mode has been overridden due to a button press and the IP address of 169.254.74.73 is being used due to the lack of response from a DHCP server. |
Programming the EEPROM
The EEPROM ships from DIYLedexpress with the firmware installed. If you buy the parts from another vendor, or you want to update the firmware to a later version, you must have a PropPlug programming tool.
The current version of the firmware is v3.04 and you can download it here.
The Programming port on the Bridge is the 4 pin header near the WizNet adapter. Match up the silk screen labels with those on the Prop Plug. You will need to externally power the bridge when programming it.
Programming Tools Required
The Propeller processor uses a different programming interface then the usual PICKIT2 or PICKIT3 device used to program the Renard PICS with their firmware. You can not use a PICKIT 2 or PICKIT3 to load the E1.31 bridge firmware. The recommended way to load the firmware in the E1.31 bridge is to use the PropPlug.
PropPlug
You can buy a PropPlug from DIYLEDExpress (Limited Stock) or find it at Parallax or Mouser.
Build your own Programming Interface
If you do not have access to a PropPlug, but you do have a PC with a true serial port, it is possible to build a simple interface to program the E1.31 bridge using simple common parts you can find from many vendors. However, the low cost PropPlug with it's USB interface works best on most modern computers.
How To Install the Firmware Programming
- Download the Parallax Propeller Tool and install it.
- Run the Propeller Tool application and it will ask of you want to associate .eeprom files with the application, Say Yes.
- You can close the Propeller Tool application and double click on the .eeprom file you downloaded or from within the application go to File->Open and change the 'Files of type' to 'Propeller Applications' and open the Bridge_v2.02.eeprom file.
- A 'Object Info' screen will open, if not already enabled click 'Show Hex'
- Connect the PropPlug to the PC and the PCB making sure that the plug is oriented correctly to match the markings on the pcb.
- Program the EEPROM on the Bridge by selecting 'Load EEPROM' and you are done.
In order to use your E1.31 Bridge, you must install and configure the software on your pc to allow your sequencing software to speak E1.31 protocol to the bridge. Click on the following links for instructions for:
Configuring the E1.31 Bridge
Once the bridge has been built and passed preliminary tests, it must be configured to operate. The configuration can be done when the bridge is connected directly to the PC or to the home network. The configuration page can be accessed via the default IP address of the controller via the browser of your choice. The default IP address of the bridge is 192.168.1.206 Open up your browser and enter http://192.168.1.206 and the setup page for the bridge will appear in the browser. If you have changed the default IP address of the bridge, you must use that address to access the setup screen.
IP Address Configuration
The default IP address and mode of the bridge when initially setup is 192.168.1.206 and is a static IP address. This can be later changed thru the web interface to what ever network address you need. Note that all E1.31 bridges and the E682 Pixel controller all use this default IP address, so if you have multiple devices on the same network, you must change the static address of the units to avoid a conflict.
Temporary Manual Address Overide
When you are troubleshooting the E1,31 bridge, it is possible to force the IP address of the unit to use another setting by using the MODE and RESET buttons at power up. If you press the MODE and RESET buttons at the same time and hold down the MODE button while you release the RESET button you can temporarily change the IP address mode. You must release the MODE button after the correct number of flashes listed below to activate that mode.
Green ACT LED Overide Flash Count | |
# of Flashes | |
Temporary Overide IP Status | |
1 | No Change. |
2 | The last saved STATIC IP address is enabled |
3 | DHCP IP address is enabled. |
System Settings
Universe Settings
Once you access the E1.31 webpage you can configure the device settings via a command line interface (original firmware) or via a webpage drop down menu (beta firmware). In the command line interface, all commands are entered on the command line and are temporary until saved. It is critical to follow all command line changes with the "SAVE 0" command to ensure your updates are saved in the device. You must then reboot the E1.31 bridge to make the changes take effect by either hitting the RESET button, or entering "BOOT 999" .
Save
Load
Boot
IP
Subnet
Gateway
DNS
If you are only using DHCP (not recommended), you can leave the static IP areas unused.
Network addressing (static or DHCP IP) is only needed to access the configuration
page with a web browser. Once configured, no IP address is needed for normal operation.
The Default IP Mode, Web Server Mode, No Data Timeout, and Test Pattern commands affect
what happens when the system starts up.
Default
DEfault n where n is 0 or 1.
Universe
Protocol
Baud
The Baud command is used to set the baud rate for each of the four output RJ45 jacks.
NOTE: This command is only used for the Renard protocol. Baud rate will not be displayed when
the DMX protocol is selected.
BAud b n Where b is the RJ45 output jack number, from 1 to 6
and n is 1 for a baud rate of 57,600 or 2 is for a baud rate of 115,200.
The Renard protocol refresh rate at 57,600bps for 512 channels is approximately 90ms and at
115,200bps the refresh rate for 512 channels is approximately 45ms.
The DMX protocol refresh rate is preset to 25ms.
Mode
"MOde" n Where n is 0 for Multicast or 1 for Unicast
TroubleShooting
Visual Inspection
Power
Hardware Reset
SOFT RESET
By pressing and releasing the RESET button, you can force a soft reboot of the E1.31 bridge and it will restart with all of the programmed parameters that you have configured the device to. This is a non destructive reboot and all settings remain intact after the reboot.
HARD RESET
It is possible to do a hard reset and erase all of the configured parameters in the E1.31 bridge and return it back to the factory default settings. To do the hard reset and lose all of your settings and return the device to the factory settings: Press the MODE and RESET buttons at the same time and hold down the MODE button while you release the RESET button. The ACT LED will flash a status code, after the ACT LED flashes 10 times, release the MODE button. This will wipe all device configuration settings and reset them to the default factory settings and will force the generation of a new random MAC ID for the unit if the MAC ID chip (IC 9) is not installed on the board.