<center>'''The Renard SS 24 measures 4" X 11"'''</center> | |||
=='''Circuit Diagram'''== | =='''Circuit Diagram'''== | ||
Revision as of 16:20, 31 October 2009
- The Renard SS24 is a PIC microcontroller based Christmas light controller with 24 solid state relay circuits incorporated into the board. The board design is based on the PIC-based 8-port dimmer concept originally developed by Phil Short. Information on the original concept can be viewed here. Generic information pertaining to current Renard designs (including maximum channel count) can be found on the Renard wiki page.
The Board
Circuit Diagram
- Key circuit components
- Connectors
- J1 – RS485 outgoing data
- Connectors
- IC Chips
- U6-U8 – PIC16F688 Microcontrollers
- M1-M24 – MOC3023 Optoisolator, triggers the triac
- IC Chips
- Resistors
- R34-R57 – Triac gate resistors. The value of these resistors in the BOM was selected for locations using 115/120 VAC power.
- Resistors
- Diagnostic LEDs
- Diagnostic LEDs
- Other Components
- T1-T24 – BTA04-700T, these are gate sensitive triacs that only require 5mA of current on the gate signal. They were selected as a dual use triac for both LEDs and regular incandescent lights.
- Other Components
- Jumpers
- JP2 – 120 ohm termination resistor enable. Normally a shunt will be installed on JP2. Remove the shunt if you are experiencing problems with incoming data.
- Jumpers
- Test Points
- GND – Ground
- ZC – Zero Cross signal
- Test Points
- The PICs (U6,U7 & U8) must be programmed with the latest firmware for the Renard SS24 to operate properly. The firmware can be found on the Renard Firmware wiki page.
Powering the Renard SS24
DC power:
- The Renard SS24 generates all the DC voltage that it requires on-board and no external DC voltage source is required.
AC Power:
- The Renard SS24 requires AC power for generation of the DC voltage, the SSR (opto/triac) circuitry and for generation of the Zero Cross signal. The information in this wiki is targeted at users who are using 115/120 VAC power.
AC Power Handling Capability
Maximum Input Load
- The Renard SS24 is divided into two banks of twelve triacs. Each bank of triacs is capable of carrying up to 15 amps of current based on the trace width used on the pcb.
Triac Loads
- Based on the pcb trace widths, each triac can handle up to two amps of current. A heat sink is highly recommended when running the triacs at two amps. Care must be taken to ensure that the total load of the twelve triacs in each bank does not exceed the rating of the fuse protecting the triac bank or 15 amps (whichever is less).
- Each bank of triacs is independently protected by its own fuse. The size of the fuse selected to use for each bank of triacs is dependent on how the Renard SS24 is connected to the AC power. When each bank of triacs has its own dedicated AC input, the size of the fuse cannot exceed the current handling capability of the input wire or 15 amps (whichever is less).
Hooking Up the Renard SS24
Data Connections
Data Cables
- Data cable for Renard SS board hookup using a RS232->RS485 converter
RS485(-) Signal to RJ45-pin 4 RS485(+) Signal to RJ45-pin 5
- Generally only a regular straight-thru CAT5 cable is required to connect Renard SS boards to other Renard boards. For the few exceptions (ie Ren24 V2.5), check the wiki page for those boards to see what their unique requirements are.
Cable Lengths
AC Power Connection
- Connection Option #1
- The size of each fuse cannot exceed the current handling capability of the orange/black wires or 15 amps (whichever is less).
- Connection Option #2
- AND
- Connection Option #3
- AND
Computer Setup
- VIXEN Settings
- Protocol Version: 1
- Parity: None
- Data bits: 8
- Stop bits: One
- If you are unsure that you have built your hardware correctly, you should follow the procedures contained in the Renard SS24 Beginner’s Setup Guide. These procedures will guide you through the steps to help setup the hardware for the first time.
- If you encounter any problems with your Renard SS24, you can go to the Troubleshooting Guide – The Renard SS24. The troubleshooting guide contains a methodical process to try to isolate problems/malfunctions and gives suggestions of what to do to fix them.