Line 513: | Line 513: | ||
=='''Troubleshooting SSR Circuitry Problems'''== | =='''Troubleshooting SSR Circuitry Problems'''== | ||
If the troubleshooting process points here, then you need to be looking at whatever external SSRs that are connected to the Renard 64XC. Basically, the functionality of the controller has been verified and the problem most likely is in the external connections or components. | |||
The Troubleshooting Guide for the SSRez can be found here. | |||
==='''Symptom(s): '''=== | ==='''Symptom(s): '''=== | ||
:*Channel remains on constantly | :*Channel remains on constantly |
Revision as of 20:41, 25 August 2010
- The following procedures require the individual to be familiar with the operation of a digital multimeter (or voltmeter/ohmmeter if you prefer). If you currently do not know how to measure resistance or how to measure voltage, please take some time now an learn these basic skills before attempting these procedures. This website provides some basic information on using multi-meters. They have different types and model and even have a few videos!
All DC voltages in this document are referenced to GND. So for all measurements, the multimeter negative (-) lead, usually black, needs to be connected to a GND point on the PCB. The best location would be the GND Test Point TP1 located near RJ45 Jack J21. The positive lead (+), usually red, gets connected to the location called out in the procedure. |
Basic Troubleshooting Info
Verify Setup
Most Common Problems
- Incorrect Vixen Settings. It cannot be emphasized enough, the Renard boards will not work correctly if Vixen is not setup correctly. Verify that you have the Vixen plug-in settings correct as compared to the Renard 64XC Controller wiki. The settings in Vixen mus match the setting used in the Renard Firmware burned onto the PICs.
Troubleshooting Flow
Troubleshooting Steps
- Turn ON AC power
- PWR LED should be lit
- Run a Vixen sequence
- If they do, go to step 15
- Turn OFF AC power
- Swap PIC chips U10 and U9
- Turn ON AC power
- Turn OFF AC power
- Swap PIC chips U10 and U8
- Turn ON AC power
- Turn OFF AC power
- Swap PIC chips U10 and U7
- Turn ON AC power
- Turn OFF AC power
- Swap PIC chips U10 and U14
- Turn ON AC power
- Turn OFF AC power
- Swap PIC chips U10 and U13
- Turn ON AC power
- Turn OFF AC power
- Swap PIC chips U10 and U12
- Turn ON AC power
- Turn OFF AC power
- Swap PIC chips U10 and U11
- Turn ON AC power
Symptom(s):
- PWR LED not lit
- IC Chips hot to the touch
Possible Problem(s):
- No Input Voltage Present
- Transformer Bad
- Voltage Regulator Bad
- Diode Polarity Wrong
- Capacitor Polarity Wrong
- LED installed backwards
- Disconnect all cables.
- In normal use, the Renard 64XC does not require a fuse. However, since this section is about "problems", it is prudent to have one installed. The best way to do this is with an in-line fuse holder on the incoming power. Mouser PN#576-150274 (holder) and PN#576-0235.300MXP (fuse) are perfect for this. The fuse used in a 300mA fuse and is rated much smaller than the power requirements of the Renard 64XC during normal use. However, using a smaller fuse here is for safety during initial power testing. If there are any problems with bridged solder pads or a bad transformer during first power application, a small fuse will blow before any permanent damage to the SSR PCB can occur.
- Connect one SSR each to J12 and J8 with a known good CAT5 cable. Now, the link is a diagram of how to check for continuity in a cable. Here is how to use a multimeter to do just that.
- Did the SSR fuse blow?
- Did the in-line fuse blow?
- If it did, go to step XXXXXX.....(???)
- Measure DC voltage at U1. This is the lead closest to U4.
- Did the PWR LED light Up?
- Measure DC voltage on the ouput side of R19. This is the end closest to the Power LED.
- If voltage is approx. 5.0 VDC, then either the LED is installed backwards or it is bad
- Measure DC voltage on the input side of R19. This is the end furtherest away from the Power LED.
- If correct, then double check the value of R19 and/or replace R19.
- Measure DC voltage at the cathodes of D1 & D2.
- Measure AC voltage between the power terminals Tab1 & Tab2.
- Voltage should be between 6.3VAC and 7.4VAC.
- If incorrect, transformer is probably bad or wired incorrectly.
- Measure AC voltage between the inline filter closest to the transformer and Tab1.
- If correct, the in-line fuse is probably bad.
- Turn OFF SSR AC power
- Remove F1 from the SSR
- Turn ON SSR AC power
- Recheck SSR AC voltage between and any N terminal.
- Bad/shorted triac
- Carefully inspect the SSR board for any possible problems with the solder connections. Fix any possible problems and then restart the troubleshooting process.
- After other attempts to fix the problem have failed, the last resort would be to remove each triac from the SSR til good power was seen with F1 installed.
- Turn OFF AC power
- Turn ON AC power
- Did the PWR LED light?
Symptom(s):
- HB and ZC LED do not flash
- FE and/or OE LEDs light
- Oscillator bad
- Zero Cross signal bad
- R1/R2 are the Wrong Value
- Vixen settings incorrect
- PIC bad
- Turn OFF AC power
- Remove PIC chip U6
- Turn ON AC power
- Replace U2
- Check the values of R1 & R2
REMINDER:
NOTE:
- Replace U5
- Turn OFF AC power
- Remove PIC chip U10
- Turn ON AC power
- Power LED should be lit and the DC voltage at the should be 5.0 (+/- .5) VDC.
- Momentarily connect a jumper (small piece of wire) between U10 IC socket pin 13 and pin 14
- HB LED should light
- Momentarily connect a jumper between U10 IC socket pin 10 and pin 14
- ZC LED should light
- Momentarily connect a jumper between U10 IC socket pin 9 and pin 14
- SD LED should light
- Momentarily connect a jumper between U10 IC socket pin 8 and pin 14
- FE LED should light
- Momentarily connect a jumper between U10 IC socket pin 7 and pin 14
- OE LED should light
- b. Check for 5.0 VDC at left side of JP3
- c. Install shunt on JP3
- d. Check for 5.0 VDC at right side of JP3 (on underside of board).
- e. Check for approx. 5.0 VDC on the pins (on underside of board) of resistor network RN1.
- If incorrect, replace RN1
- If any (but not all) of the LEDs in steps 6 thru 10 did not light, measure the DC voltage at the appropriate location on the IC socket for U10. The voltage measured at each location should be approximately 3.0-3.5 VDC.
Diagnostic LED Measure DC voltage at HB U10 IC socket pin 13 ZC U10 IC socket pin 10 SD U10 IC socket pin 9 FE U10 IC socket pin 8 OE U10 IC socket pin 7
Symptom(s):
- Bad triac
- Triac in Backwards
- Bad opto
- Opto/MOC in Backwards
- Bad/missed Solder Joints
- Turn OFF AC power
- Check the right side fuse
- If not, go to step 21
- Turn ON AC power
- Test lights should be OFF
- Turn OFF AC power
- Install PIC chip U6
- Turn OFF AC power
- Turn OFF AC power
- Turn ON AC power
SAFETY NOTICE:
- Bad triac
- It should be 5 VDC
- If not, go to step 37
- Remove PIC chip U7
- Turn ON AC power
- Turn OFF AC power
- Install PIC chip U7
- Turn OFF AC power
- Turn OFF AC power
- Turn ON AC power
SAFETY NOTICE:
- Bad triac
- Remove PIC chip U8
- Turn ON AC power
- Turn OFF AC power
- Install PIC chip U8
- Turn OFF AC power
- Turn OFF AC power
- Turn ON AC power
SAFETY NOTICE:
- Bad triac
- Turn OFF AC power
- Turn ON AC power
- Is the test light still ON?