REN 32 Controller Board
- The REN 32 is the latest 32 channel Microchip 16F688 based PIC microcontroller Christmas light controller that can be used with up to 32 AC or DC solid state relay () . The board design is based on the PIC-based 8-port dimmer concept originally developed by Phil Short. Information on the original concept can be viewed here. Generic information pertaining to current Renard designs (including maximum channel count) can be found on the Renard wiki page. It is capable of running on either 115vac or 230vac main power to the board.
- This controller follows the Renard Standardized Series (SS) controller design: a design effort to standardize the board layouts for Renard based systems and to establish a standardized list of components to use in Renard designs. Some of the goals of the Renard SS design effort were:
- Completely self-contained controller board. All that is needed to start using the board is a data input and an AC power source. No external DC voltage supply or externally generated ZC is needed.
The Board
Board Availability
Circuit Diagram
- The schematic diagram can be found HERE
- Key circuit components
- Connectors
Connectors | ||
Connector | Type | Function |
J1 | RJ45 | RS485 outgoing data |
J2 | RJ45 | RS232/RS485 incoming data |
J3 | RJ45 | Control Signal to SSR Channels 1-4 |
J4 | RJ45 | Control Signal to SSR Channels 5-8 |
J5 | RJ45 | Control Signal to SSR Channels 9-12 |
J6 | RJ45 | Control Signal to SSR Channels 13-16 |
J7 | RJ45 | Control Signal to SSR Channels 17-20 |
J8 | RJ45 | Control Signal to SSR Channels 21-24 |
J9 | RJ45 | Control Signal to SSR Channels 25-28 |
J10 | RJ45 | Control Signal to SSR Channels 29-32 |
AC Power In | Screw Terminals | AC Power Feed |
- IC Chips
- U2 – H11AA1 Optocoupler, used to generate the Zero Cross signal for ACSSRs
- U6-U9 – PIC16F688 Microcontrollers
- IC Chips
- Diagnostic LEDs
- Diagnostic LEDs
- NOTE: The following Diagnostic LEDs will only function when a jumper is placed on JP3 and U6 has the diagnostic firmware loaded.
- Other Components
- Other Components
- Jumpers
- JP2 – 120 ohm termination resistor enable. Normally a shunt will be installed on JP2 when receiving RS485 data. Remove the shunt if you are experiencing problems with incoming data.
- Jumpers
- Main Voltage – You must provide either a jumper across the 2 horizontal jumpers to enable the board to run on 115vac, or one jumper across the 230vac jumper to allow the board to run on 230vac.
- Test Points
- GND – Ground
- ZC – Zero Cross signal
- Test Points
- The PICs (U6,U7 U8& U9) must be programmed with the correct firmware for the board to operate correctly. There are two types of firmware available: Operational and Diagnostic. The Operational firmware is what you need for normal board operation. The Diagnostic firmware is a troubleshooting aid to use when there are problems with the board.
- Renard SS Operational Firmware:
- Renard SS Operational Firmware.asm – source code that needs to be compiled
- Renard SS Diagnostic Firmware:
- Renard SS Diagnostic Firmware.asm – source code that needs to be compiled
- DMX Firmware:
- Since there are many options available with the Renard DMX firmware it is impractical to post a dedicated Renard SS board version here. Users desiring to use DMX should get the firmware here.
Powering the REN 32
- Input power requirements: An AC source. The board can be powered be either 115vac or 230vac depending on the Main Power Jumper settings.
DC power:
- The Ren32 generates all the DC voltage that it requires on-board and no external DC voltage source is required.
AC Power:
- The REN 32 requires AC power for generation of the DC voltage, the off board SSR (opto/triac) circuitry and for generation of the Zero Cross signal.
AC Power Handling Capability
Maximum Input Load
- Since the REN 32 uses off board SSRs, the power the board can control is based on their capabilities. See the DCSSR and the ACSSR wiki for possible ssr designs to use with this board. Since the REN 32 is actually 4 banks of 8 channels you can mix and match both AC and DC SSRs in groups of 8. All channels in a bank must be the same type (AC or DC).
- The board has a safety fuse for protecting the ac mains voltage on the board.
- The BOM calls for a 1 amp fuse.
Hooking Up the REN 32
J1 and J2-Renard Input and Output
The two RJ45 Connectors J1&J2 near the top right of the board are used to bring data signals to and from the board. J1 on the left side is the signal input from the PC or previous Renard controller. J2 on the right side is the output to be daisy-chained to the next Renard controller. The pins on these connectors are used as follows:
Serial Data Connector Pin Assignments | ||
Pin # | RJ45 Connector | |
J1 Input | J2 Output | |
1,2 | GND | GND |
3 | Pin 3 is tied to J2 Pin 3 | Pin 3 is tied to J1 Pin 3 |
4 | Data- (Rx) | Data- (Tx) |
5 | Data+ (Rx) | Data+ (Tx) |
6 | GND | GND |
7,8 | Pins 7&8 are tied together to J2 Pins 7&8 | Pins 7&8 are tied together to J1 Pins 7&8 |
Data Connections
Data Cables
Cable Lengths
AC Power Connection
- AC Power Connection
- The AC power source is connected to the two screw terminals on the left side of the board.
- THE CORRECT POWER JUMPERS MUST BE INSTALLED FOR THE CORRECT LINE VOLTAGE BEING SUPPLIED TO THE BOARD!!!
Power Connections | ||
Pin # | Input Voltage | |
115VAC | 230VAC | |
"AC" Top |
Neutral (White Wire) |
Hot Wire |
"IN" Bottom |
Hot (Black Wire) |
Hot Wire |
SSR Connections
- Connecting SSRs to the REN 32
- The REN 32 provides control signals to external Solid State Relays (SSRs) to switch power on/off and to dim the lights connected to the SSRs.
Output Jack Pin Assignments | ||
Pin # | ||
Signal | ||
1 | +5VDC | |
2 | First Output Channel | |
3 | Not Connected | |
4 | Second Output Channel | |
5 | Not Connected | |
6 | Third Output Channel | |
7 | Signal Ground | |
6 | Fourth Output Channel |
- Each of the 8 output jacks control 4 channels each.
Output Jack Channel Assignments | ||
Jack # | ||
Channels | ||
J3 | 1-4 | |
J4 | 5-8 | |
J5 | 9-12 | |
J6 | 13-16 | |
J7 | 17-20 | |
J8 | 21-24 | |
J9 | 25-28 | |
J10 | 29-32 |
Configuring the jumpers on Renard SS boards
- JP1 & JP2 Configuraton
- JP1 installed
- JP2 not installed
- JP1 not installed
- JP3 Configuraton
Computer Setup
- VIXEN Settings
- Protocol Version: 1
- Parity: None
- Data bits: 8
- Stop bits: One
- If you are unsure that you have built your hardware correctly, you should follow the procedures contained in the REN 32 Beginners Setup Guide. These procedures will guide you through the steps to help setup the hardware for the first time.
- If you encounter any problems with your REN 32, you can go to the Troubleshooting Guide For The REN 32. The troubleshooting guide contains a methodical process to try to isolate problems/malfunctions and gives suggestions of what to do to fix them.
- Board Availability Information
